Item
|
Specifications
|
Input power
|
Number of phases, voltage, frequency
|
200V level: single phase 220~240V, 50/60Hz
|
400V level: three-phase 380/400/415/440/460V, 50/60Hz
|
Allowed voltage variation
|
-15%~+10%
|
Allowed frequency variation
|
-5%~+5%
|
Instantaneous voltage Reduce tolerance
|
200V level: Continue to run above AC150V; continue to run for 15ms when the rated input drops below AC150V. Post undervoltage protection
|
400V level: Continue to run above AC300V; when the rated input state drops below AC300V, continue to run for 15ms and then provide undervoltage protection.
|
Basic features
|
highest floor
|
40th floor
|
Elevator running speed
|
≤ 4.00m/s
|
Group control quantity
|
≤ 8 units
|
communication method
|
CAN bus serial communication
|
Operation function
|
See Product Feature List in Introduction
|
Drive characteristics
|
control method
|
Vector control with PG card
|
Starting torque
|
Depending on load, up to 200%
|
Speed control range
|
1:1000(Vector control with PG card)
|
Speed control accuracy
|
±0.05%(Vector control with PG card 25±10℃)
|
Torque limit
|
200% Rated torque
|
Torque accuracy
|
±5%
|
Frequency control range
|
0~99Hz
|
Frequency accuracy
|
±0.1%
|
Frequency setting resolution
|
0.01Hz/99Hz
|
Output frequency resolution (calculated resolution)
|
0.01Hz
|
No load starting compensation
|
When the size of the elevator is unknown, according to the direction in which the elevator will run, apply appropriate torque to the motor and command a smooth start, minimizing the car slippage at the start moment and increasing the comfort of the elevator during startup.
|
Braking torque
|
150%(external braking resistor), built-in braking unit
|
Acceleration and deceleration time
|
0.1~8s
|
carrier frequency
|
2~ 16kHz
|
Battery operation
|
In the event of a power outage, the elevator relies on battery power to level the elevator at low speed.
|
PG interface
|
PG card type
|
Set open, push-pull, differential, SIN/COS, Endat absolute value type
|
PG card signal frequency division output
|
OA, OB orthogonal
|
Input, output signal
|
Optocoupler input control power supply
|
Isolated 24VDC
|
Low voltage optocoupler isolated input
|
24 switching values, the optocoupler control signal is an isolated 24VDC, power input signal
|
High voltage optocoupler isolated input
|
3-way switch
|
Relay output
|
6 -way normally open contacts, single pole single throw, 5A contact switching capability, contact load (resistive): 5A250VAC or 5A28VDC
|
USB interface
|
Mobile phone debugging
|
CAN communication interface
|
2-way (car top communication, parallel or group control)
|
MOD Communication
|
2-way (outbound call communication, community monitoring or Internet of Things)
|
Analog input port
|
1-way single-ended or differential input, input voltage range -10V~+10V, accuracy 0.1%
|
Protective function
|
Motor overload protection
|
The protection curve of the motor can be parameterized
|
Frequency converter overload
|
150% rated current for 60 seconds; 200% rated current for 10 seconds
|
Short circuit protection
|
When any two phases on the output side are short-circuited and cause overcurrent, the drive controller is protected.
|
Input phase loss protection
|
If the input phase is lost, the output will be shut down to protect the drive controller.
|
Output phase loss protection
|
If the output phase is missing, the output will be shut down to protect the drive controller.
|
Overvoltage threshold
|
Bus voltage 800V (380V series), 400V (220V series)
|
Undervoltage threshold
|
Bus voltage 350V (200V series), 150V (220V series)
|
Instantaneous power outage compensation
|
Protection above 15ms
|
Heat sink overheated
|
Protection via thermistor device
|
prevent stalling
|
Stall protection when the speed deviation is greater than 15% of the rated speed during operation
|
Pulse encoder failure
|
PG wire break
|
Braking unit protection
|
Automatically detect brake unit anomalies and protect
|
Module protection
|
Overcurrent, short circuit, overheating protection
|
Current sensor protection
|
Self-test at power-on
|
Speed abnormality protection
|
Detected by encoder
|
Input voltage over-voltage protection
|
400V level is greater than 725V, 200V level is greater than 360V, detected when stopped
|
Output ground protection
|
During operation, if any phase is short-circuited to ground, the output will be shut down to protect the inverter.
|
Output imbalance protection
|
When an unbalanced output three-phase current is detected during operation, the output is shut down to protect the inverter.
|
Braking resistor short circuit protection
|
Detection while braking
|
Speed abnormality protection
|
According to the different stages of elevator operation (acceleration, deceleration, constant speed), rapid protection is provided for elevator speed abnormalities.
|
Run time limiter protection
|
During operation, protection when passing through the floor exceeds the specified time
|
Leveling switch fault protection
|
Protection caused by leveling switch failure
|
EEPROM failure
|
Self-test at power-on
|
Display
|
Small keypad
|
3-digit LED display, enabling some debugging functions
|
Operation panel
|
5-digit LED display allows viewing, modifying most parameters and monitoring system status
|
PC software
|
Connect the system and computer to view and modify system status comprehensively and intuitively
|