Item |
AT20 |
Basic function |
Control Mode |
V/F control
Sensorless flux vector control (SVC)(Above 3.7K)
Close-loop vector control (FVC)(Above 3.7KW) |
Maximum frequency |
0~600Hz |
Carrier frequency |
0.5kHz~8kHz
The carrier frequency is automatically adjusted based on the load features. |
Input frequency resolution |
Digital setting:0.01Hz
Analog setting: Maximum frequency x 0.025% |
Start torque |
G Type:0.5Hz/150%(SVC);
P Type:0.5Hz/100% |
Speed range |
1:100 (SVC) |
Speed stability accuracy |
±0.5% (SVC) |
Overload capacity |
G Type:60s for 150% of the rated current,
3s for 180% of the rated current.
P Type:60s for 120% of the rated current,
3s for 150% of the rated current. |
Torque boost |
Auto-boost;
Customized boost: 0.1%~30.0% |
V/F Curve |
Straight-line V/F curve
Multi-point V/F curve
N-power V/F curve (1.2-power, 1.4-power, 1.6-power,
1.8-power, square) |
V/F separation |
2 types: complete separation; half separation |
Ramp Mode |
Straight-line ramp.
Four groups of acceleration/deceleration time with the range of 0.00`6500.0s |
DC braking |
DC braking frequency:0.00Hz~Maximum frequency
Braking time:0.0s~36.0s
Braking action current value:0.0%~100.0% |
JOG control |
JOG frequency range:0.00Hz~50.00Hz。
JOG acceleration/deceleration time: 0.0s~6500.0s。 |
Simple PLC、Multiple preset speeds |
It implements up to 16 speeds via the simple PLC function or combination of terminal states |
Onboard PID |
It realizes process-controlled closed loop control system easily |
Auto voltage regulation(AVR) |
It can keep constant output voltage automatically when the mains voltage changes |
Overvoltage/overcurrent stall control |
The current and voltage are limited automatically during the running process so as to avoid frequent tripping due to over voltage/over current |
Rapid current limit |
It helps to avoid frequent over current faults of the AC drive. |
Torque limit and control |
It can limit the torque automatically and prevent frequent over current tripping during the running process. Torque control can be implemented in the FVC mode. |
Individualized functions |
High performance |
Control of asynchronous motor are implemented through the high-performance current vector control technology |
Rapid dip ride through |
The load feedback energy compensates the voltage reduction so that the AC drive can continue to run for a short time |
Rapid current limit |
It helps to avoid frequent over current faults of the AC drive. |
Timing control |
Timing range: 0.0Min~6500.0Min |
Communication methods |
R S - 4 8 5 |
Running |
Command source |
Operation panel/Control terminals/Serial communication port
You can perform switchover between these sources in various ways. |
Frequency source |
There are ten frequency sources.
Digital setting, analog voltage setting, analog current setting, pulse setting, serial port setting.
You can perform switchover in various ways. |
Auxiliary frequency source |
There are ten auxiliary frequency sources. It can implement fine tuning of auxiliary frequency and frequency synthesis. |
Input terminal |
Standard:4 digital input terminals(Below 5.5KW)/6 digital input terminals(Above 7.5KW)
1 analog input terminal(Below 5.5KW)/2 analog input terminals(Above 7.5KW);
1 voltage input (only support for 0~10V, above 7.5KW),1 voltage input(0~10V) or current input (4~20mA) |
Output terminal |
1 High-speed pulse output terminal (Open-collector)(Above 3.7KW)
1 replay output terminal (Below 5.5KW)/2 replay output terminals(Above 7.5KW)
1 analog output terminal(3.7KW~5.5KW)/2 analog output terminal(Above 7.5KW), Support for 4~20mA current output or 0~10V voltage output |
Display and operation panel |
LED display |
It displays the parameters |
Key locking and function selection |
It can lock the keys partially or completely and define the function range of some keys so as to prevent mal-function. |
Protection mode |
Motor short-circuit detection at power-on, input/output phase loss protection, over current protection, over voltage protection, under voltage protection, overheat protection and overload protection |
Environment |
Installation location |
Indoor, free from direct sunlight, dust, corrosive gas, combustible gas, oil smoke, vapor, drip or salt. |
Altitude |
Lower than 1000m |
Ambient temperature |
-10℃~+40℃( de-rated if the ambient temperature is between 40℃~50℃) |
Humidity |
Less than 95%RH,without condensing |
Vibration |
Less than 5.9m/s2(0.6g) |
Storage temperature |
-20℃~+60℃ |